No Levelled GCode file is created
Re: No Levelled GCode file is created
OK, I have uploaded the fix. If you re-download the source or main file for 0.8.3 it should work with pretty much any RPF. Let me know if not.
GastonGagnon
Post by GastonGagnon »
You may have answered this previously but it is not clear to me why you couldn't simply assume that the machine positioned the tool close enough and use the x and y coordinates called for in the PFG GCode file? The RPF could be limited to log the Z values of each probe measurement.
Gaston
Hi Gaston,
Mach3 gives me no option as to what gets logged in the probe file and what doesnt, it simply lists all axis values whenever the probe makes contact. In the gcode of the PFG it opens and closes the RPF with M40 / M41, I get no say as to what gets logged and in what format.
I could indeed do things as you say but that would require both the RPF and PFG to be read back into Autoleveller in order to get the assumed x and y values from the PFG file. Currently, only the RPF is needed to be read back into AL. In short its simpler this way :)
Does it work OK?
kvnrydberg
Post by kvnrydberg »
I didn't have any luck with the fix. I didn't select the option to create only the probe file, though, so this may be why. I leveled the engraving file, then tried to use the probe log so created on my pocketing file. The results were the same as before. I'll upload the RPF and PFG files. Oops. The system won't let me upload for some reason.
Here's the PFG:
(AutoLeveller, Version: 0.8.3, http://autoleveller.co.uk)
(Copyright 2013-2014 James Hawthorne PhD)
(Original GCode file: HPFTopProfile v1.nc)
(Creation date: 22/07/2014 time: 21:17)
(AutoLeveller comes with ABSOLUTELY NO WARRANTY; for details, see sections 11 and 12 of the GPLv2)
(prerequisites)
(1. need a working probe)
(2. Zero your Z axis on or just above the surface)
(Note: The first probe will touch off Z to 0.000 when it first touches to copper, )
(all other probe values are relative to this first point)
G20 (Inches)
G90 (absolute distance mode, not incremental)
G0 Z1(Move clear of the board first)
G0 X0.4 Y0.4(Move to bottom left corner)
G0 Z0.05(Quick move to probe clearance height)
G31 Z-0.0625 F5
G0 Z0.05
G31 Z-0.0625 F2.5
M40 (Begins a probe log file, when the window appears, enter a name for the log file such as "RawProbeLog.txt")
G0 Z0.05
G0 X0.4 Y0.4
G31 Z-0.0625 F5
#500=#2002
G0 Z0.05
G0 X0.781818 Y0.4
G31 Z-0.0625 F5
#501=#2002
G0 Z0.05
G0 X1.163636 Y0.4
G31 Z-0.0625 F5
#502=#2002
G0 Z0.05
G0 X1.545455 Y0.4
G31 Z-0.0625 F5
#503=#2002
G0 Z0.05
G0 X1.927273 Y0.4
G31 Z-0.0625 F5
#504=#2002
G0 Z0.05
G0 X2.309091 Y0.4
G31 Z-0.0625 F5
#505=#2002
G0 Z0.05
G0 X2.690909 Y0.4
G31 Z-0.0625 F5
#506=#2002
G0 Z0.05
G0 X3.072727 Y0.4
G31 Z-0.0625 F5
#507=#2002
G0 Z0.05
G0 X3.454545 Y0.4
G31 Z-0.0625 F5
#508=#2002
G0 Z0.05
G0 X3.836364 Y0.4
G31 Z-0.0625 F5
#509=#2002
G0 Z0.05
G0 X4.218182 Y0.4
G31 Z-0.0625 F5
#510=#2002
G0 Z0.05
G0 X4.6 Y0.4
G31 Z-0.0625 F5
#511=#2002
G0 Z0.05
G0 X4.6 Y0.791667
G31 Z-0.0625 F5
#523=#2002
G0 Z0.05
G0 X4.218182 Y0.791667
G31 Z-0.0625 F5
#522=#2002
G0 Z0.05
G0 X3.836364 Y0.791667
G31 Z-0.0625 F5
#521=#2002
G0 Z0.05
G0 X3.454545 Y0.791667
G31 Z-0.0625 F5
#520=#2002
G0 Z0.05
G0 X3.072727 Y0.791667
G31 Z-0.0625 F5
#519=#2002
G0 Z0.05
G0 X2.690909 Y0.791667
G31 Z-0.0625 F5
#518=#2002
G0 Z0.05
G0 X2.309091 Y0.791667
G31 Z-0.0625 F5
#517=#2002
G0 Z0.05
G0 X1.927273 Y0.791667
G31 Z-0.0625 F5
#516=#2002
G0 Z0.05
G0 X1.545455 Y0.791667
G31 Z-0.0625 F5
#515=#2002
G0 Z0.05
G0 X1.163636 Y0.791667
G31 Z-0.0625 F5
#514=#2002
G0 Z0.05
G0 X0.781818 Y0.791667
G31 Z-0.0625 F5
#513=#2002
G0 Z0.05
G0 X0.4 Y0.791667
G31 Z-0.0625 F5
#512=#2002
G0 Z0.05
G0 X0.4 Y1.183333
G31 Z-0.0625 F5
#524=#2002
G0 Z0.05
G0 X0.781818 Y1.183333
G31 Z-0.0625 F5
#525=#2002
G0 Z0.05
G0 X1.163636 Y1.183333
G31 Z-0.0625 F5
#526=#2002
G0 Z0.05
G0 X1.545455 Y1.183333
G31 Z-0.0625 F5
#527=#2002
G0 Z0.05
G0 X1.927273 Y1.183333
G31 Z-0.0625 F5
#528=#2002
G0 Z0.05
G0 X2.309091 Y1.183333
G31 Z-0.0625 F5
#529=#2002
G0 Z0.05
G0 X2.690909 Y1.183333
G31 Z-0.0625 F5
#530=#2002
G0 Z0.05
G0 X3.072727 Y1.183333
G31 Z-0.0625 F5
#531=#2002
G0 Z0.05
G0 X3.454545 Y1.183333
G31 Z-0.0625 F5
#532=#2002
G0 Z0.05
G0 X3.836364 Y1.183333
G31 Z-0.0625 F5
#533=#2002
G0 Z0.05
G0 X4.218182 Y1.183333
G31 Z-0.0625 F5
#534=#2002
G0 Z0.05
G0 X4.6 Y1.183333
G31 Z-0.0625 F5
#535=#2002
G0 Z0.05
G0 X4.6 Y1.575
G31 Z-0.0625 F5
#547=#2002
G0 Z0.05
G0 X4.218182 Y1.575
G31 Z-0.0625 F5
#546=#2002
G0 Z0.05
G0 X3.836364 Y1.575
G31 Z-0.0625 F5
#545=#2002
G0 Z0.05
G0 X3.454545 Y1.575
G31 Z-0.0625 F5
#544=#2002
G0 Z0.05
G0 X3.072727 Y1.575
G31 Z-0.0625 F5
#543=#2002
G0 Z0.05
G0 X2.690909 Y1.575
G31 Z-0.0625 F5
#542=#2002
G0 Z0.05
G0 X2.309091 Y1.575
G31 Z-0.0625 F5
#541=#2002
G0 Z0.05
G0 X1.927273 Y1.575
G31 Z-0.0625 F5
#540=#2002
G0 Z0.05
G0 X1.545455 Y1.575
G31 Z-0.0625 F5
#539=#2002
G0 Z0.05
G0 X1.163636 Y1.575
G31 Z-0.0625 F5
#538=#2002
G0 Z0.05
G0 X0.781818 Y1.575
G31 Z-0.0625 F5
#537=#2002
G0 Z0.05
G0 X0.4 Y1.575
G31 Z-0.0625 F5
#536=#2002
G0 Z0.05
G0 X0.4 Y1.966667
G31 Z-0.0625 F5
#548=#2002
G0 Z0.05
G0 X0.781818 Y1.966667
G31 Z-0.0625 F5
#549=#2002
G0 Z0.05
G0 X1.163636 Y1.966667
G31 Z-0.0625 F5
#550=#2002
G0 Z0.05
G0 X1.545455 Y1.966667
G31 Z-0.0625 F5
#551=#2002
G0 Z0.05
G0 X1.927273 Y1.966667
G31 Z-0.0625 F5
#552=#2002
G0 Z0.05
G0 X2.309091 Y1.966667
G31 Z-0.0625 F5
#553=#2002
G0 Z0.05
G0 X2.690909 Y1.966667
G31 Z-0.0625 F5
#554=#2002
G0 Z0.05
G0 X3.072727 Y1.966667
G31 Z-0.0625 F5
#555=#2002
G0 Z0.05
G0 X3.454545 Y1.966667
G31 Z-0.0625 F5
#556=#2002
G0 Z0.05
G0 X3.836364 Y1.966667
G31 Z-0.0625 F5
#557=#2002
G0 Z0.05
G0 X4.218182 Y1.966667
G31 Z-0.0625 F5
#558=#2002
G0 Z0.05
G0 X4.6 Y1.966667
G31 Z-0.0625 F5
#559=#2002
G0 Z0.05
G0 X4.6 Y2.358333
G31 Z-0.0625 F5
#571=#2002
G0 Z0.05
G0 X4.218182 Y2.358333
G31 Z-0.0625 F5
#570=#2002
G0 Z0.05
G0 X3.836364 Y2.358333
G31 Z-0.0625 F5
#569=#2002
G0 Z0.05
G0 X3.454545 Y2.358333
G31 Z-0.0625 F5
#568=#2002
G0 Z0.05
G0 X3.072727 Y2.358333
G31 Z-0.0625 F5
#567=#2002
G0 Z0.05
G0 X2.690909 Y2.358333
G31 Z-0.0625 F5
#566=#2002
G0 Z0.05
G0 X2.309091 Y2.358333
G31 Z-0.0625 F5
#565=#2002
G0 Z0.05
G0 X1.927273 Y2.358333
G31 Z-0.0625 F5
#564=#2002
G0 Z0.05
G0 X1.545455 Y2.358333
G31 Z-0.0625 F5
#563=#2002
G0 Z0.05
G0 X1.163636 Y2.358333
G31 Z-0.0625 F5
#562=#2002
G0 Z0.05
G0 X0.781818 Y2.358333
G31 Z-0.0625 F5
#561=#2002
G0 Z0.05
G0 X0.4 Y2.358333
G31 Z-0.0625 F5
#560=#2002
G0 Z0.05
G0 X0.4 Y2.75
G31 Z-0.0625 F5
#572=#2002
G0 Z0.05
G0 X0.781818 Y2.75
G31 Z-0.0625 F5
#573=#2002
G0 Z0.05
G0 X1.163636 Y2.75
G31 Z-0.0625 F5
#574=#2002
G0 Z0.05
G0 X1.545455 Y2.75
G31 Z-0.0625 F5
#575=#2002
G0 Z0.05
G0 X1.927273 Y2.75
G31 Z-0.0625 F5
#576=#2002
G0 Z0.05
G0 X2.309091 Y2.75
G31 Z-0.0625 F5
#577=#2002
G0 Z0.05
G0 X2.690909 Y2.75
G31 Z-0.0625 F5
#578=#2002
G0 Z0.05
G0 X3.072727 Y2.75
G31 Z-0.0625 F5
#579=#2002
G0 Z0.05
G0 X3.454545 Y2.75
G31 Z-0.0625 F5
#580=#2002
G0 Z0.05
G0 X3.836364 Y2.75
G31 Z-0.0625 F5
#581=#2002
G0 Z0.05
G0 X4.218182 Y2.75
G31 Z-0.0625 F5
#582=#2002
G0 Z0.05
G0 X4.6 Y2.75
G31 Z-0.0625 F5
#583=#2002
G0 Z0.05
G0 X4.6 Y3.141667
G31 Z-0.0625 F5
#595=#2002
G0 Z0.05
G0 X4.218182 Y3.141667
G31 Z-0.0625 F5
#594=#2002
G0 Z0.05
G0 X3.836364 Y3.141667
G31 Z-0.0625 F5
#593=#2002
G0 Z0.05
G0 X3.454545 Y3.141667
G31 Z-0.0625 F5
#592=#2002
G0 Z0.05
G0 X3.072727 Y3.141667
G31 Z-0.0625 F5
#591=#2002
G0 Z0.05
G0 X2.690909 Y3.141667
G31 Z-0.0625 F5
#590=#2002
G0 Z0.05
G0 X2.309091 Y3.141667
G31 Z-0.0625 F5
#589=#2002
G0 Z0.05
G0 X1.927273 Y3.141667
G31 Z-0.0625 F5
#588=#2002
G0 Z0.05
G0 X1.545455 Y3.141667
G31 Z-0.0625 F5
#587=#2002
G0 Z0.05
G0 X1.163636 Y3.141667
G31 Z-0.0625 F5
#586=#2002
G0 Z0.05
G0 X0.781818 Y3.141667
G31 Z-0.0625 F5
#585=#2002
G0 Z0.05
G0 X0.4 Y3.141667
G31 Z-0.0625 F5
#584=#2002
G0 Z0.05
G0 X0.4 Y3.533333
G31 Z-0.0625 F5
#596=#2002
G0 Z0.05
G0 X0.781818 Y3.533333
G31 Z-0.0625 F5
#597=#2002
G0 Z0.05
G0 X1.163636 Y3.533333
G31 Z-0.0625 F5
#598=#2002
G0 Z0.05
G0 X1.545455 Y3.533333
G31 Z-0.0625 F5
#599=#2002
G0 Z0.05
G0 X1.927273 Y3.533333
G31 Z-0.0625 F5
#600=#2002
G0 Z0.05
G0 X2.309091 Y3.533333
G31 Z-0.0625 F5
#601=#2002
G0 Z0.05
G0 X2.690909 Y3.533333
G31 Z-0.0625 F5
#602=#2002
G0 Z0.05
G0 X3.072727 Y3.533333
G31 Z-0.0625 F5
#603=#2002
G0 Z0.05
G0 X3.454545 Y3.533333
G31 Z-0.0625 F5
#604=#2002
G0 Z0.05
G0 X3.836364 Y3.533333
G31 Z-0.0625 F5
#605=#2002
G0 Z0.05
G0 X4.218182 Y3.533333
G31 Z-0.0625 F5
#606=#2002
G0 Z0.05
G0 X4.6 Y3.533333
G31 Z-0.0625 F5
#607=#2002
G0 Z0.05
G0 X4.6 Y3.925
G31 Z-0.0625 F5
#619=#2002
G0 Z0.05
G0 X4.218182 Y3.925
G31 Z-0.0625 F5
#618=#2002
G0 Z0.05
G0 X3.836364 Y3.925
G31 Z-0.0625 F5
#617=#2002
G0 Z0.05
G0 X3.454545 Y3.925
G31 Z-0.0625 F5
#616=#2002
G0 Z0.05
G0 X3.072727 Y3.925
G31 Z-0.0625 F5
#615=#2002
G0 Z0.05
G0 X2.690909 Y3.925
G31 Z-0.0625 F5
#614=#2002
G0 Z0.05
G0 X2.309091 Y3.925
G31 Z-0.0625 F5
#613=#2002
G0 Z0.05
G0 X1.927273 Y3.925
G31 Z-0.0625 F5
#612=#2002
G0 Z0.05
G0 X1.545455 Y3.925
G31 Z-0.0625 F5
#611=#2002
G0 Z0.05
G0 X1.163636 Y3.925
G31 Z-0.0625 F5
#610=#2002
G0 Z0.05
G0 X0.781818 Y3.925
G31 Z-0.0625 F5
#609=#2002
G0 Z0.05
G0 X0.4 Y3.925
G31 Z-0.0625 F5
#608=#2002
G0 Z0.05
G0 X0.4 Y4.316667
G31 Z-0.0625 F5
#620=#2002
G0 Z0.05
G0 X0.781818 Y4.316667
G31 Z-0.0625 F5
#621=#2002
G0 Z0.05
G0 X1.163636 Y4.316667
G31 Z-0.0625 F5
#622=#2002
G0 Z0.05
G0 X1.545455 Y4.316667
G31 Z-0.0625 F5
#623=#2002
G0 Z0.05
G0 X1.927273 Y4.316667
G31 Z-0.0625 F5
#624=#2002
G0 Z0.05
G0 X2.309091 Y4.316667
G31 Z-0.0625 F5
#625=#2002
G0 Z0.05
G0 X2.690909 Y4.316667
G31 Z-0.0625 F5
#626=#2002
G0 Z0.05
G0 X3.072727 Y4.316667
G31 Z-0.0625 F5
#627=#2002
G0 Z0.05
G0 X3.454545 Y4.316667
G31 Z-0.0625 F5
#628=#2002
G0 Z0.05
G0 X3.836364 Y4.316667
G31 Z-0.0625 F5
#629=#2002
G0 Z0.05
G0 X4.218182 Y4.316667
G31 Z-0.0625 F5
#630=#2002
G0 Z0.05
G0 X4.6 Y4.316667
G31 Z-0.0625 F5
#631=#2002
G0 Z0.05
G0 X4.6 Y4.708333
G31 Z-0.0625 F5
#643=#2002
G0 Z0.05
G0 X4.218182 Y4.708333
G31 Z-0.0625 F5
#642=#2002
G0 Z0.05
G0 X3.836364 Y4.708333
G31 Z-0.0625 F5
#641=#2002
G0 Z0.05
G0 X3.454545 Y4.708333
G31 Z-0.0625 F5
#640=#2002
G0 Z0.05
G0 X3.072727 Y4.708333
G31 Z-0.0625 F5
#639=#2002
G0 Z0.05
G0 X2.690909 Y4.708333
G31 Z-0.0625 F5
#638=#2002
G0 Z0.05
G0 X2.309091 Y4.708333
G31 Z-0.0625 F5
#637=#2002
G0 Z0.05
G0 X1.927273 Y4.708333
G31 Z-0.0625 F5
#636=#2002
G0 Z0.05
G0 X1.545455 Y4.708333
G31 Z-0.0625 F5
#635=#2002
G0 Z0.05
G0 X1.163636 Y4.708333
G31 Z-0.0625 F5
#634=#2002
G0 Z0.05
G0 X0.781818 Y4.708333
G31 Z-0.0625 F5
#633=#2002
G0 Z0.05
G0 X0.4 Y4.708333
G31 Z-0.0625 F5
#632=#2002
G0 Z0.05
G0 X0.4 Y5.1
G31 Z-0.0625 F5
#644=#2002
G0 Z0.05
G0 X0.781818 Y5.1
G31 Z-0.0625 F5
#645=#2002
G0 Z0.05
G0 X1.163636 Y5.1
G31 Z-0.0625 F5
#646=#2002
G0 Z0.05
G0 X1.545455 Y5.1
G31 Z-0.0625 F5
#647=#2002
G0 Z0.05
G0 X1.927273 Y5.1
G31 Z-0.0625 F5
#648=#2002
G0 Z0.05
G0 X2.309091 Y5.1
G31 Z-0.0625 F5
#649=#2002
G0 Z0.05
G0 X2.690909 Y5.1
G31 Z-0.0625 F5
#650=#2002
G0 Z0.05
G0 X3.072727 Y5.1
G31 Z-0.0625 F5
#651=#2002
G0 Z0.05
G0 X3.454545 Y5.1
G31 Z-0.0625 F5
#652=#2002
G0 Z0.05
G0 X3.836364 Y5.1
G31 Z-0.0625 F5
#653=#2002
G0 Z0.05
G0 X4.218182 Y5.1
G31 Z-0.0625 F5
#654=#2002
G0 Z0.05
G0 X4.6 Y5.1
G31 Z-0.0625 F5
#655=#2002
G0 Z0.05
G0 X0.4 Y0.4 Z1
M41 (Closes the opened log file)
(Set S value to ensure Speed has a value otherwise the spindle will not start on an M3 command)
S20000
(The program will pause to allow the probe to be detached)
(press cycle start to resume from current line)
M0
(The original mill file is now rewritten with z depth replaced with a)
(bilinear interpolated value based on the initial probing)
( Made using CamBam - http://www.cambam.co.uk )
( HPFTopProfile v1 7/22/2014 8:57:13 PM )
( T1 : 60 degree V-Cutter )
G20 G90 G91.1 G64 G40
( Profile1 )
T1 M6
G17
G0 Z0.03
M3 S24000
G0 X2.31 Y1.7111
#102=[#541+0.347489*#553-0.347489*#541]
#101=[#542+0.347489*#554-0.347489*#542]
#100=[#102+0.002381*#101-0.002381*#102]
And here's the RPF:
0.40012,0.40008,-0.00025
0.78254,0.40008,0.00175
1.16471,0.39983,0.00275
1.54639,0.40008,0.00325
1.92831,0.40008,0.00400
2.31023,0.39983,0.00425
2.69190,0.40008,0.00350
3.07357,0.40008,0.00275
3.45574,0.39983,0.00125
3.83717,0.40008,-0.00050
4.21934,0.40008,-0.00225
4.60101,0.39983,-0.00500
4.60101,0.79223,-0.00400
4.21834,0.79223,-0.00200
3.83617,0.79223,-0.00050
3.45474,0.79223,0.00125
3.07257,0.79198,0.00225
2.69090,0.79223,0.00325
2.30923,0.79223,0.00375
1.92706,0.79223,0.00375
1.54563,0.79223,0.00350
1.16346,0.79223,0.00325
0.78204,0.79198,0.00225
0.39987,0.79223,0.00200
0.40012,1.18388,0.00275
0.78254,1.18388,0.00275
1.16471,1.18363,0.00325
1.54639,1.18388,0.00300
1.92831,1.18388,0.00325
2.31023,1.18388,0.00300
2.69190,1.18388,0.00225
3.07357,1.18363,0.00200
3.45549,1.18388,0.00025
3.83742,1.18388,-0.00100
4.21934,1.18388,-0.00225
4.60101,1.18363,-0.00400
4.60101,1.57552,-0.00375
4.21809,1.57552,-0.00225
3.83642,1.57552,-0.00075
3.45449,1.57552,0.00025
3.07282,1.57552,0.00175
2.69090,1.57552,0.00225
2.30898,1.57552,0.00325
1.92731,1.57552,0.00350
1.54563,1.57552,0.00325
1.16346,1.57527,0.00350
0.78179,1.57552,0.00325
0.40012,1.57552,0.00400
0.39987,1.96717,0.00450
0.78279,1.96717,0.00375
1.16471,1.96717,0.00375
1.54639,1.96717,0.00300
1.92831,1.96717,0.00300
2.30998,1.96742,0.00250
2.69190,1.96667,0.00200
3.07382,1.96667,0.00175
3.45549,1.96667,0.00000
3.83742,1.96667,-0.00125
4.21909,1.96667,-0.00250
4.60101,1.96667,-0.00425
4.60101,2.35882,-0.00475
4.21834,2.35882,-0.00250
3.83642,2.35882,-0.00100
3.45449,2.35882,0.00075
3.07282,2.35882,0.00175
2.69090,2.35882,0.00225
2.30898,2.35882,0.00350
1.92731,2.35882,0.00350
1.54538,2.35882,0.00375
1.16371,2.35882,0.00400
0.78179,2.35882,0.00425
0.40012,2.35882,0.00524
0.39987,2.75046,0.00549
0.78279,2.75046,0.00425
1.16471,2.75046,0.00400
1.54639,2.75071,0.00350
1.92831,2.75046,0.00350
2.30998,2.75046,0.00325
2.69190,2.75046,0.00225
3.07382,2.75046,0.00150
3.45549,2.75046,0.00075
3.83742,2.75046,-0.00125
4.21909,2.75071,-0.00300
4.60101,2.75046,-0.00574
4.60101,3.14211,-0.00475
4.21834,3.14211,-0.00225
3.83642,3.14236,-0.00025
3.45449,3.14211,0.00100
3.07282,3.14211,0.00250
2.69090,3.14211,0.00300
2.30898,3.14236,0.00350
1.92731,3.14211,0.00375
1.54538,3.14211,0.00375
1.16371,3.14236,0.00400
0.78179,3.14211,0.00425
0.40012,3.14211,0.00599
0.39987,3.53376,0.00524
0.78279,3.53401,0.00450
1.16446,3.53376,0.00425
1.54664,3.53376,0.00400
1.92831,3.53376,0.00400
2.30998,3.53401,0.00375
2.69190,3.53376,0.00325
3.07382,3.53376,0.00225
3.45549,3.53376,0.00125
3.83742,3.53401,-0.00050
4.21909,3.53376,-0.00175
4.60101,3.53376,-0.00400
4.60101,3.92540,-0.00400
4.21834,3.92565,-0.00150
3.83642,3.92540,-0.00025
3.45449,3.92565,0.00150
3.07257,3.92540,0.00250
2.69090,3.92540,0.00325
2.30923,3.92565,0.00375
1.92731,3.92540,0.00400
1.54538,3.92540,0.00400
1.16371,3.92565,0.00400
0.78179,3.92540,0.00400
0.39987,3.92565,0.00475
0.40012,4.31705,0.00375
0.78279,4.31730,0.00350
1.16446,4.31705,0.00350
1.54664,4.31730,0.00350
1.92831,4.31705,0.00350
2.30998,4.31730,0.00350
2.69190,4.31705,0.00300
3.07382,4.31730,0.00250
3.45549,4.31705,0.00100
3.83742,4.31730,-0.00050
4.21909,4.31705,-0.00225
4.60101,4.31730,-0.00475
4.60101,4.70870,-0.00574
4.21834,4.70895,-0.00300
3.83642,4.70870,-0.00075
3.45449,4.70895,0.00125
3.07257,4.70870,0.00250
2.69090,4.70895,0.00350
2.30923,4.70870,0.00425
1.92731,4.70895,0.00400
1.54538,4.70870,0.00350
1.16371,4.70895,0.00300
0.78179,4.70870,0.00225
0.39987,4.70895,0.00225
0.40012,5.10034,0.00125
0.78254,5.10059,0.00175
1.16471,5.10059,0.00325
1.54639,5.10034,0.00375
1.92831,5.10059,0.00450
2.31023,5.10034,0.00475
2.69190,5.10059,0.00400
3.07357,5.10059,0.00350
3.45574,5.10034,0.00125
3.83717,5.10059,-0.00125
4.21934,5.10059,-0.00350
4.60101,5.10034,-0.00674
OK, I saw the problem with your RPF and have relaxed the tolerance a bit. Everything seems OK with my test files including your RPF.
Please re-download AL, try again and let me know if it works.
If there are further problems it may be necessary to make changes to the GUI and upload the PFG with the RPF as Gaston hinted at.
kvnrydberg
I started out with a small test file and it worked as described. But when I tried it with my circuit it did not. I didn't use the same PFG as before because my circuit has changed a bit. I'll upload the new ones in case you want to take a look.
RPF.txt
(4 KiB) Downloaded 3564 times
PFG.nc
(11.02 KiB) Downloaded 8307 times
I can see the problem I think and will work on it today. It is important to iron out these kinks as the probe files are an important addition to AL.
Thanks for your efforts.
UPDATE: I have just updated AL and uploaded the fix. Please download and try again. Let me know how you get on :)
ADDITIONAL NOTE: I made some changes to the GUI yesterday so it might look different. The GUI changes are not finished yet but are purely cosmetic so dont be alarmed.
kvnrydberg
The new fix has been working. This helps me out a bunch. Thank you. If I run into any problems I'll let you know.
Excellent. No problem.
I am wondering though, what level of accuracy you have on your Z axis given the differences between mine and your RPF with the X and Y axis. If your Z axis is giving you inaccurate numbers then you may get a poor result when it comes to actually levelling.
It may be worth your time checking backlash on your machine to improve matters. I have anti-backlash nuts on each of my screws which all but eliminates backlash and this may be a reason for the differences between mine and your RPF results. Do you have anti-backlash nuts on your machine? It might be worth thinking about adding if not.
just a thought,
kvnrydberg
Hello James. The Z-axis on my machine is fairly accurate, typically <.0005" over the length of travel. I use anti backlash nuts also and have measured the backlash on my Z axis to be around .001". Even so, I still use backlash compensation in Mach3. Like we were talking about, I think backlash comp is the reason for the differences. I'm puzzled as to why an inaccurate Z-axis would lead to discrepancies in the x,y pos in the probe file. Nevertheless, using a 60 degree v-bit and a PCB jig which I haven't even bothered to level in reference to my machine, the results using autoleveller have been stellar. It's a fantastically useful program, and you have given hobbyists a real tool for making professional circuit boards consistently.